An in-building emergency voice/alarm communications system draws 0.80 A standby and 6.0 A in alarm. What alarm duration must the battery calculation use after the 24-hour standby?

Exactly one answer is correct.

Show solution

Correct answer to question 3003

  • D: 15 minutes

Explanation

EVACS secondary power must support 24 hours of standby followed by 15 minutes of alarm at maximum connected load. Non-voice systems use 5 minutes. For this load the alarm portion is 6.0 x 0.25 = 1.5 Ah.