Question 3002 of 297 · NICET Fire Alarm Systems Level III
A system draws 0.30 A in standby and 1.80 A in alarm. With 24 hours standby, 5 minutes alarm, and no margin, what is the required battery capacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3002
- C: 7.35 Ah
Explanation
Standby: 0.30 x 24 = 7.20 Ah. Alarm: 1.80 x 5/60 = 0.15 Ah. Total 7.35 Ah. Designers then apply the aging correction factor (1.25 in the 2022 and 2025 editions) before choosing a battery size.
More questions: Submittal Preparation and System Layout
- 3003An in-building emergency voice/alarm communications system draws 0.80 A standby and 6.0 A in alarm. What alarm duration must the battery calculation use after the 24-hour standby?
- 3004In a battery calculation, which current values should be used for each device?
- 3005A 24 VDC notification circuit has 10 strobes drawing a total of 1.5 A. The farthest strobe is 300 ft from the panel on 14 AWG solid wire with 3.07 ohms per 1,000 ft. What is the approximate voltage drop at the end?
- 3006A strobe circuit is designed to start at a worst-case panel source voltage of 20.4 V. The strobes are listed for 16 to 33 V. What is the maximum allowable voltage drop on the circuit?
- 3007A 12 AWG stranded circuit has a resistance of 1.98 ohms per 1,000 ft. The load is 2.0 A at the end of a 250 ft run. What is the voltage drop?
- 3008A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?