When must the first sensitivity test of a smoke detector be performed after installation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6002
- B: Within one year, then every alternate year
Explanation
NFPA 72 and OFC 907.8.3 require sensitivity to be checked within one year after installation and every alternate year after that.