Question 6026 of 183 · Ohio Fire Alarm Certification Exam
A building has 300 non restorable spot type heat detectors that are 15 years old. How many must go to a lab if the owner does not replace them all?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6026
- D: 6
Explanation
NFPA 72 requires 2 detectors per 100 to be lab tested: 300 / 100 x 2 = 6. If any fail, more are tested.