When must valve regulated lead acid (VRLA) batteries in a fire alarm system be replaced at the latest?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6028
- B: On the replacement date set by the equipment manufacturer
Explanation
NFPA 72 ties VRLA replacement to the equipment manufacturer replacement date, checked against the month and year marking. Batteries are also replaced earlier when they fail the periodic tests, such as the 3 year load test.