What is the minimum secondary power capacity for a protected premises fire alarm system without voice evacuation?

Exactly one answer is correct.

Show solution

Correct answer to question 3026

  • C: 24 hours of standby followed by 5 minutes of alarm

Explanation

Secondary power must run the system under quiescent load for 24 hours and then operate all alarm notification appliances for 5 minutes. Voice evacuation systems need 15 minutes of alarm at maximum connected load.