Question 3027 of 153 · Oklahoma Fire Alarm Technician Exam
A fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3027
- C: Automatic smoke detection at the control unit
Explanation
Where the control unit is in an area not continuously occupied, automatic smoke detection must protect the location so a fire there is detected before it destroys the panel. Heat detection is allowed where smoke detection is unsuitable.
More questions: System Layout and NFPA 72 Requirements
- 3028Within what time after an initiating device activates must the fire alarm control unit activate the alarm notification appliances?
- 3029What is the maximum time permitted for alarm verification on a smoke detector circuit?
- 3030Under positive alarm sequence, how long does trained staff have to acknowledge the alarm at the control unit?
- 3031A waterflow alarm initiating device must produce an alarm signal within what time after flow equal to one sprinkler starts?
- 3032A valve supervisory switch must signal an off normal condition within what movement of the valve?
- 3033For elevator shunt trip, where must heat detectors be located relative to sprinklers in the elevator machine room or hoistway?