A sleeping room strobe is mounted 18 in below the ceiling. What minimum effective intensity is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3024
- B: 177 cd
Explanation
In sleeping areas, a visible appliance mounted within 24 in of the ceiling needs at least 177 cd, because smoke may obscure it. Mounted more than 24 in below the ceiling, 110 cd is required.