A waterflow alarm initiating device must produce an alarm signal within what time after flow equal to one sprinkler starts?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3031
- B: 90 seconds
Explanation
NFPA 72 requires the waterflow alarm initiating device to signal within 90 seconds after a flow equal to or greater than that of the smallest sprinkler begins.