Question 3030 of 153 · Oklahoma Fire Alarm Technician Exam
Under positive alarm sequence, how long does trained staff have to acknowledge the alarm at the control unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3030
- D: 15 seconds
Explanation
Positive alarm sequence gives trained staff 15 seconds to acknowledge and then up to 180 seconds to investigate and reset. If not acknowledged in 15 seconds, the alarm sounds immediately.
More questions: System Layout and NFPA 72 Requirements
- 3031A waterflow alarm initiating device must produce an alarm signal within what time after flow equal to one sprinkler starts?
- 3032A valve supervisory switch must signal an off normal condition within what movement of the valve?
- 3033For elevator shunt trip, where must heat detectors be located relative to sprinklers in the elevator machine room or hoistway?
- 3001What is the nominal spacing used for spot-type smoke detectors on a smooth, flat ceiling when no other spacing is required by the manufacturer?
- 3002A spot-type smoke detector is to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be?
- 3003A spot-type heat detector is mounted on a sidewall. What mounting zone is permitted?