Question 3032 of 153 · Oklahoma Fire Alarm Technician Exam
A valve supervisory switch must signal an off normal condition within what movement of the valve?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3032
- C: Two revolutions of the handwheel or one fifth of the stem travel
Explanation
The supervisory signal must occur within two revolutions of the handwheel or when the stem has moved one fifth of its travel from the normal position, and must not restore until the valve is fully back to normal.
More questions: System Layout and NFPA 72 Requirements
- 3033For elevator shunt trip, where must heat detectors be located relative to sprinklers in the elevator machine room or hoistway?
- 3001What is the nominal spacing used for spot-type smoke detectors on a smooth, flat ceiling when no other spacing is required by the manufacturer?
- 3002A spot-type smoke detector is to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be?
- 3003A spot-type heat detector is mounted on a sidewall. What mounting zone is permitted?
- 3004A heat detector has a listed spacing of 50 ft. What is the maximum distance from a wall to the nearest detector on a smooth ceiling?
- 3005A heat detector with a listed spacing of 50 ft is installed on a smooth ceiling 15 ft high. Using the ceiling height reduction factor of 0.77 for ceilings over 14 ft up to 16 ft, what is the adjusted spacing?