Question 5002 of 153 · Oklahoma Fire Alarm Technician Exam
When must the first sensitivity test of a system smoke detector be performed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5002
- B: Within 1 year after installation, then every alternate year
Explanation
Sensitivity is checked within 1 year after installation and every alternate year after that. Once two consecutive tests show the detector is in range, the interval may be extended up to 5 years.
More questions: Inspection, Testing and Service
- 5003Which method is NOT acceptable to measure the sensitivity of a smoke detector?
- 5004Nonrestorable fixed temperature spot-type heat detectors have been in service for 15 years. What does NFPA 72 require?
- 5005How should a restorable spot-type heat detector be functionally tested?
- 5006Single and multiple station smoke alarms must be replaced no later than how long after the date of manufacture?
- 5007Before testing a monitored fire alarm system, whom must the technician notify?
- 5008After a software change on a fire alarm system, what portion of initiating devices not directly affected must be tested?