Question 5003 of 153 · Oklahoma Fire Alarm Technician Exam
Which method is NOT acceptable to measure the sensitivity of a smoke detector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5003
- B: Spraying aerosol smoke into the detector and seeing whether it alarms
Explanation
Aerosol or smoke in a can only proves the detector alarms, which is a functional test. It does not measure sensitivity, which requires calibrated methods or panel based sensitivity readings.