Before testing a monitored fire alarm system, whom must the technician notify?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5007
- D: The supervising station and the building occupants or facility staff who would receive alarms
Explanation
Before testing, the supervising station, fire department where required, and facility occupants and staff who receive signals are notified so the test signals are not treated as real alarms. They are notified again when testing ends.
More questions: Inspection, Testing and Service
- 5008After a software change on a fire alarm system, what portion of initiating devices not directly affected must be tested?
- 5009How long must inspection and test records be kept?
- 5010Under NFPA 101, a required fire alarm system will be out of service for more than 4 hours in a 24 hour period. What is required?
- 5011What document is prepared at acceptance to record the installed system details, and is kept for the life of the system?
- 5012What is the frequency for the visual inspection of fire alarm control units in a monitored system?
- 5013How often must a sealed lead acid fire alarm battery receive its load voltage and charger tests?