Question 5004 of 153 · Oklahoma Fire Alarm Technician Exam
Nonrestorable fixed temperature spot-type heat detectors have been in service for 15 years. What does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5004
- D: Replace 2 of every 100 detectors and send them for laboratory testing
Explanation
Nonrestorable detectors cannot be heat tested in place. After 15 years, 2 detectors per 100 (or fraction) are removed and laboratory tested; if one fails, more are tested.