How should a restorable spot-type heat detector be functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5005
- A: With a heat source per the manufacturer's instructions, without damaging it
Explanation
Restorable heat detectors are tested with a heat source that operates them without damage, following the manufacturer's method. Open flames are not acceptable test methods.
More questions: Inspection, Testing and Service
- 5006Single and multiple station smoke alarms must be replaced no later than how long after the date of manufacture?
- 5007Before testing a monitored fire alarm system, whom must the technician notify?
- 5008After a software change on a fire alarm system, what portion of initiating devices not directly affected must be tested?
- 5009How long must inspection and test records be kept?
- 5010Under NFPA 101, a required fire alarm system will be out of service for more than 4 hours in a 24 hour period. What is required?
- 5011What document is prepared at acceptance to record the installed system details, and is kept for the life of the system?