How many conductors may share a device box is determined by which NEC rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1140
- D: Box fill calculations based on box volume and conductor size
Explanation
NEC box fill rules set the volume needed for each conductor by size, plus allowances for devices and clamps. Overfilled boxes lead to damaged insulation and ground faults.