An addressable monitor module will supervise a sprinkler tamper switch. What is the module's job?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1141
- A: To report the switch's contact status to the panel as an addressed point
Explanation
A monitor (input) module connects a contact device, such as a tamper or waterflow switch, to the signaling line circuit so the panel can identify it by address and report alarm, supervisory or trouble.