The site-specific software of a control unit was changed. Besides the functions known to be affected, how many other initiating devices must be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- D: At least 10 percent, up to a maximum of 50 devices
Explanation
After a software change, all functions known to be affected are tested, plus at least 10 percent of initiating devices not directly affected, up to 50 devices, to catch unexpected effects.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2024What is the purpose of the 100 percent acceptance test on a new fire alarm system?
- 2025At acceptance testing, how are installation conductors checked for unwanted voltages?
- 2026To measure loop resistance of an initiating device circuit during acceptance testing, what is done at the far end of the circuit?
- 2027A technician checks fire alarm conductors for isolation from ground. What is being looked for?
- 2028You need to megger (insulation resistance test) a new fire alarm circuit. What must be done first?
- 2029When measuring the voltage on a notification appliance circuit with a multimeter, how is the meter connected?