Correct answer to question 2070
- D: With a heat source that raises the temperature quickly, per the manufacturer
Explanation
A rate-of-rise element responds to a fast temperature increase, typically around 15 F per minute. A slow heat-up tests only the fixed-temperature part, if any. Aerosol is for smoke detectors.