Question 2069 of 299 · NICET Fire Alarm Systems Level I
An area of a building is having repeated smoke detector nuisance alarms after construction work. What is a likely cause?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2069
- D: Dust contamination inside the sensing chambers
Explanation
Construction dust gets into the chambers and raises the background reading, which can lead to nuisance alarms. The detectors need cleaning or replacement.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2070How is a rate-of-rise heat detector correctly tested?
- 2071When testing a duct smoke detector, what else must be checked besides the alarm response to smoke?
- 2072What should happen when a duct smoke detector that controls air movement goes into alarm during a test?
- 2073How is a manual fire alarm box normally tested?
- 2074During the annual test of a horn/strobe circuit, what should the technician verify?
- 2075Sound level measurements of notification appliances are required by NFPA 72 mainly at which tests?