Question 2071 of 299 · NICET Fire Alarm Systems Level I
When testing a duct smoke detector, what else must be checked besides the alarm response to smoke?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2071
- C: That airflow through the sampling tube is within the listed range
Explanation
Duct detectors need a minimum air velocity or pressure difference across the sampling tubes to draw a sample. Technicians verify this per the manufacturer as well as the alarm response.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2072What should happen when a duct smoke detector that controls air movement goes into alarm during a test?
- 2073How is a manual fire alarm box normally tested?
- 2074During the annual test of a horn/strobe circuit, what should the technician verify?
- 2075Sound level measurements of notification appliances are required by NFPA 72 mainly at which tests?
- 2076A sound level meter used for fire alarm audibility tests should meet which instrument class?
- 2077Which tool is used to deliver test aerosol to a ceiling smoke detector from the floor?