During acceptance testing of a Class A initiating circuit, how is the redundant path proven?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2090
- B: Open the circuit at a point and confirm devices on both sides still alarm
Explanation
For Class A and Class X circuits, an open is introduced and the technician verifies that the panel shows a trouble and that devices beyond the open can still send an alarm.