Question 2014 of 172 · Texas Fire Alarm License Exam
In the three-pulse temporal pattern, each cycle consists of three 0.5-second on phases separated by 0.5-second off phases, followed by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2014
- A: a 1.5-second off phase
Explanation
Each cycle is on 0.5 s, off 0.5 s, on 0.5 s, off 0.5 s, on 0.5 s, then off 1.5 s, for a 4-second cycle.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)