Question 2019 of 172 · Texas Fire Alarm License Exam
On a smooth ceiling, spot-type smoke detectors are permitted a nominal spacing of
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2019
- B: 30 feet
Explanation
Spot-type smoke detectors on smooth ceilings may use a nominal spacing of 30 ft, with all points on the ceiling within 0.7 times that spacing of a detector.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2020A spot-type smoke detector mounted on a sidewall must be located
- 2021Spot-type heat detectors on a smooth ceiling must be located so that all points on the ceiling are within what distance of a detector?
- 2022A heat detector has a listed spacing of 50 ft. On a smooth flat ceiling, the maximum distance from the detector to a wall is
- 2023Spot-type heat detectors mounted on a sidewall must be located
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be
- 2025NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?