Question 2018 of 172 · Texas Fire Alarm License Exam
In a sleeping room, a wall-mounted visible appliance with the top of its lens less than 24 inches below the ceiling must have a minimum rating of
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2018
- A: 177 candela
Explanation
Sleeping area strobes within 24 in. of the ceiling need 177 cd. If the lens is 24 in. or more below the ceiling, 110 cd is permitted.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2019On a smooth ceiling, spot-type smoke detectors are permitted a nominal spacing of
- 2020A spot-type smoke detector mounted on a sidewall must be located
- 2021Spot-type heat detectors on a smooth ceiling must be located so that all points on the ceiling are within what distance of a detector?
- 2022A heat detector has a listed spacing of 50 ft. On a smooth flat ceiling, the maximum distance from the detector to a wall is
- 2023Spot-type heat detectors mounted on a sidewall must be located
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be