Question 2020 of 172 · Texas Fire Alarm License Exam
A spot-type smoke detector mounted on a sidewall must be located
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2020
- C: within 12 inches of the ceiling, measured to the top of the detector
Explanation
Wall-mounted spot-type smoke detectors must be between the ceiling and 12 in. down from the ceiling to the top of the detector.