Question 2023 of 172 · Texas Fire Alarm License Exam
Spot-type heat detectors mounted on a sidewall must be located
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- B: between 4 and 12 inches below the ceiling
Explanation
Heat detectors on sidewalls are placed between 4 in. and 12 in. from the ceiling to the top of the detector; on the ceiling they must be at least 4 in. from the wall.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be
- 2025NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?
- 2026Duct smoke detectors used for HVAC control
- 2027Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over
- 2028The operable part of a manual fire alarm box must be mounted
- 2029Manual fire alarm boxes must be located within 5 feet of each exit doorway on each floor, and the travel distance to the nearest box must not exceed