NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2025
- D: 36 inches
Explanation
Strong air movement can dilute or deflect smoke. NFPA 72 annex guidance keeps spot-type smoke detectors out of direct airflow and about 36 in. from supply diffusers or return openings.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2026Duct smoke detectors used for HVAC control
- 2027Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over
- 2028The operable part of a manual fire alarm box must be mounted
- 2029Manual fire alarm boxes must be located within 5 feet of each exit doorway on each floor, and the travel distance to the nearest box must not exceed
- 2030How often must spot-type smoke detectors receive a functional test after acceptance?
- 2031Smoke detector sensitivity must be checked within one year after installation and then