Question 2034 of 172 · Texas Fire Alarm License Exam
After a modification to an existing system, reacceptance testing must include all affected devices plus
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2034
- A: 10 percent of unaffected initiating devices, up to 50 devices
Explanation
Reacceptance testing covers all functions and devices affected by the change and at least 10 percent of initiating devices not directly affected, up to a maximum of 50.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2035Nonrestorable fixed-temperature spot-type heat detectors that have been in service for 15 years must be
- 2036Under NFPA 72, records of inspection, testing and maintenance must be kept
- 2037A circuit that keeps operating to all devices after a single open, and also after a single ground fault or wire-to-wire short, is classified as
- 2038A Class B initiating device circuit with a single open conductor will
- 2039Pathway survivability Level 2 is generally provided by
- 2040At the control unit, an alarm signal from an initiating device must cause notification appliances to activate within