Nonrestorable fixed-temperature spot-type heat detectors that have been in service for 15 years must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2035
- B: replaced or sampled with 2 detectors per 100 sent for laboratory testing
Explanation
After 15 years, these detectors must be replaced or two detectors per 100 must be removed and sent to a laboratory for testing.