A circuit that keeps operating to all devices after a single open, and also after a single ground fault or wire-to-wire short, is classified as
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2037
- D: Class X
Explanation
Class X adds tolerance of wire-to-wire shorts to the Class A redundant path. Class A tolerates a single open but not a short; Class B has no redundant path.