Under positive alarm sequence, trained staff must acknowledge the alarm signal within
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2051
- B: 15 seconds, then have 180 seconds to investigate
Explanation
Positive alarm sequence requires acknowledgment within 15 seconds and allows up to 180 seconds of investigation before the system must activate notification and off-premises signals.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2052On a peaked ceiling, a row of spot-type smoke detectors must be located on or near the peak, within what horizontal distance of the peak?
- 2053Which smoke detector type generally responds faster to slow, smoldering fires that produce large visible particles?
- 2054Ionization smoke detectors are generally most responsive to
- 2055A rate-of-rise heat detector typically operates when the temperature rises faster than about
- 2056Under the heat detector temperature classification table, an intermediate classification detector (175 to 249 degrees F) carries what color code?
- 2057The temperature rating of a fixed-temperature heat detector must be at least how much above the maximum expected ambient ceiling temperature?