On a peaked ceiling, a row of spot-type smoke detectors must be located on or near the peak, within what horizontal distance of the peak?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2052
- C: 36 inches
Explanation
For peaked and sloped ceilings, spot-type smoke detectors are placed within 36 in. horizontally of the peak, but not closer than 4 in. vertically.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)