The temperature rating of a fixed-temperature heat detector must be at least how much above the maximum expected ambient ceiling temperature?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2057
- D: 20 degrees F
Explanation
Detectors must be rated at least 20 degrees F (11 degrees C) above the maximum expected ceiling temperature to avoid unwanted alarms.