A rate-of-rise heat detector typically operates when the temperature rises faster than about
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2055
- B: 12 to 15 degrees F per minute
Explanation
Rate-of-rise detectors respond to a rapid temperature increase, commonly listed at about 12 to 15 degrees F (6.7 to 8.3 degrees C) per minute, regardless of the starting temperature.