The branch circuit supplying fire alarm equipment must NOT be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2070
- A: supplied through a GFCI or an AFCI
Explanation
Article 760 prohibits supplying fire alarm branch circuits through ground fault or arc fault circuit interrupters, which could trip and disable the system.