On a Class A or Class B pathway, how must a single ground fault be treated?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1008
- A: Operation continues, and the ground fault is annunciated as trouble
Explanation
Both Class A and Class B pathways must keep their operational capability during a single ground fault, and the ground condition must produce a trouble signal so it can be corrected before a second fault causes a failure.