Which pathway class was created specifically for modern Ethernet infrastructure serving fire alarm or emergency communication devices?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1007
- A: Class N
Explanation
Class N covers Ethernet pathways with end to end verification and, where more than one device is served, a primary and a redundant pathway. Loss of communication between endpoints must be annunciated as trouble.