Under the separation rule for Class A and Class X pathways, what minimum separation applies between outgoing and return pathways run vertically?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1010
- D: 1 ft
Explanation
Outgoing and return pathways must be separated by at least 1 ft (300 mm) where installed vertically and at least 4 ft (1.22 m) where installed horizontally. Limited exceptions apply, for example short drops to individual devices.
More questions: Installation
- 1011Under the separation rule for Class A and Class X pathways, what minimum separation applies between outgoing and return pathways run horizontally?
- 1012What does pathway survivability Level 0 require?
- 1013A pathway is run in metal raceway in a building fully protected by an NFPA 13 sprinkler system. Which survivability level does this describe?
- 1014Which method meets pathway survivability Level 2?
- 1015What distinguishes survivability Level 3 from Level 2?