For a Class A circuit, why does NFPA 72 require the outgoing and return conductors to be routed separately?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1009
- B: So one event cannot easily damage both paths
Explanation
The redundant path of a Class A or Class X circuit only adds reliability if a single fire, impact, or cut cannot reach both legs. The code therefore sets minimum separation distances between outgoing and return pathways, with limited exceptions.
More questions: Installation