Question 1012 of 344 · NICET Fire Alarm Systems Level II
What does pathway survivability Level 0 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1012
- B: No special provisions for survivability
Explanation
Level 0 pathways have no survivability requirements. Level 1 relies on sprinkler protection plus metal raceway, Level 2 uses 2 hour rated cable or enclosures, and Level 3 combines Level 2 methods with full sprinkler protection.