A pathway is run in metal raceway in a building fully protected by an NFPA 13 sprinkler system. Which survivability level does this describe?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1013
- D: Level 1
Explanation
Level 1 survivability is achieved in a building fully sprinklered per NFPA 13 with the interconnecting pathways installed in metal raceway. Level 2 requires 2 hour rated protection, and Level 3 requires both sprinklers and Level 2 methods.