Question 1014 of 344 · NICET Fire Alarm Systems Level II
Which method meets pathway survivability Level 2?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1014
- B: A 2 hour rated circuit integrity (CI) cable
Explanation
Level 2 survivability uses 2 hour rated methods: CI cable, a 2 hour fire rated cable system (electrical circuit protective system), a 2 hour rated enclosure or protected area, or an approved performance alternative.
More questions: Installation
- 1015What distinguishes survivability Level 3 from Level 2?
- 1016Under NFPA 70 Article 760, what are the three types of listed power-limited fire alarm cable, from most to least fire resistive in application?
- 1017A PLFA cable will be installed in a ceiling space used for environmental air (plenum). Which cable type is suitable without a raceway?
- 1018A PLFA circuit runs vertically through floors in a shaft. Which cable type is the lowest rating suitable for that riser application?
- 1019Which cable may be substituted for FPL in a general purpose PLFA application?
- 1020What minimum separation does NFPA 70 generally require between PLFA conductors and electric light or power conductors when neither is in a raceway or a permitted cable sheath?