Question 1015 of 344 · NICET Fire Alarm Systems Level II
What distinguishes survivability Level 3 from Level 2?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1015
- B: Level 3 also requires full sprinkler protection
Explanation
Level 3 requires the building to be fully sprinklered per NFPA 13 in addition to the 2 hour rated protection methods of Level 2. It combines both protection strategies.
More questions: Installation
- 1016Under NFPA 70 Article 760, what are the three types of listed power-limited fire alarm cable, from most to least fire resistive in application?
- 1017A PLFA cable will be installed in a ceiling space used for environmental air (plenum). Which cable type is suitable without a raceway?
- 1018A PLFA circuit runs vertically through floors in a shaft. Which cable type is the lowest rating suitable for that riser application?
- 1019Which cable may be substituted for FPL in a general purpose PLFA application?
- 1020What minimum separation does NFPA 70 generally require between PLFA conductors and electric light or power conductors when neither is in a raceway or a permitted cable sheath?
- 1021May PLFA conductors and 120 V power conductors share the same raceway?