A PLFA circuit runs vertically through floors in a shaft. Which cable type is the lowest rating suitable for that riser application?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1018
- A: FPLR
Explanation
Riser applications require FPLR or a higher rated substitute such as FPLP. FPL is a general use cable and is not rated to prevent fire travel floor to floor.