A PLFA cable will be installed in a ceiling space used for environmental air (plenum). Which cable type is suitable without a raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1017
- A: FPLP
Explanation
Only plenum rated cable such as FPLP (or a permitted substitute such as CMP) may be installed exposed in other spaces used for environmental air. FPLR and FPL do not have the low smoke and flame spread rating required there.
More questions: Installation
- 1018A PLFA circuit runs vertically through floors in a shaft. Which cable type is the lowest rating suitable for that riser application?
- 1019Which cable may be substituted for FPL in a general purpose PLFA application?
- 1020What minimum separation does NFPA 70 generally require between PLFA conductors and electric light or power conductors when neither is in a raceway or a permitted cable sheath?
- 1021May PLFA conductors and 120 V power conductors share the same raceway?
- 1022Which circuit types may share a cable with PLFA conductors under NFPA 70?
- 1023What does NFPA 70 require for the branch circuit supplying a fire alarm control unit?