What minimum separation does NFPA 70 generally require between PLFA conductors and electric light or power conductors when neither is in a raceway or a permitted cable sheath?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1020
- B: 2 in.
Explanation
PLFA circuit conductors must be kept at least 50 mm (2 in.) from electric light, power, Class 1, and NPLFA conductors unless a raceway, a permitted cable sheath, or a fixed nonconductor provides separation.