May PLFA conductors and 120 V power conductors share the same raceway?

Exactly one answer is correct.

Show solution

Correct answer to question 1021

  • B: No, unless a specific exception for associated equipment applies

Explanation

PLFA circuits must not be placed in the same raceway, cable, or enclosure as electric light or power circuits. Narrow exceptions allow power conductors that only connect to the same equipment, with separation inside the enclosure.