Question 1021 of 344 · NICET Fire Alarm Systems Level II
May PLFA conductors and 120 V power conductors share the same raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1021
- B: No, unless a specific exception for associated equipment applies
Explanation
PLFA circuits must not be placed in the same raceway, cable, or enclosure as electric light or power circuits. Narrow exceptions allow power conductors that only connect to the same equipment, with separation inside the enclosure.
More questions: Installation
- 1022Which circuit types may share a cable with PLFA conductors under NFPA 70?
- 1023What does NFPA 70 require for the branch circuit supplying a fire alarm control unit?
- 1024Where must the location of the fire alarm branch circuit disconnecting means be documented?
- 1025NFPA 70 requires fire alarm circuits to be identified at terminal and junction locations. What is the purpose?
- 1026How must exposed fire alarm cables above a suspended ceiling be supported under NFPA 70?
- 1027What must be done with the accessible portion of abandoned fire alarm cable?