What does NFPA 70 require for the branch circuit supplying a fire alarm control unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1023
- D: No GFCI or AFCI, and a red marked disconnect labeled FIRE ALARM CIRCUIT
Explanation
The fire alarm branch circuit must not be supplied through ground fault or arc fault circuit interrupters, so nuisance trips cannot drop the system. The disconnect must have red identification, be accessible only to qualified personnel, and be identified as FIRE ALARM CIRCUIT.